@mcduff wrote:


The OP is @govindsankar; @santo_13 was just giving advice. Excluding the name mistake, you are correct, this project seems a little advanced for the OP.


Sorry santo_13! My excuse is that it was the end of the day and I was tired...

0 Kudos
Message 21 of 53
(962 Views)

I think one problem here is that the task is not well defined.

 

I made a "Windows" system for a portable spectroscopy measurements that contained a Class 4 laser. However, all of the safety in the system was hardware based. I was able to read the digital lines with a cheap NI DIO board of the hardware interlocks easily and respond to them. The lesson here is that software had no control over the interlocks and if Windows/software crashed then no safety issue. If the hardware interlocks were not engaged no matter how many times I sent a command to fire the laser, it would not fire. Safety did not depend on software.

 

Does the hydraulic press here have hardware interlocks that will protect a user in spite of the software? If so the lack of experience may not be a problem. But if the system is relying on software for safety without any hardware,  I would be concerned.

Message 22 of 53
(950 Views)

@mcduff wrote:

I think one problem here is that the task is not well defined.

 

I made a "Windows" system for a portable spectroscopy measurements that contained a Class 4 laser. However, all of the safety in the system was hardware based. I was able to read the digital lines with a cheap NI DIO board of the hardware interlocks easily and respond to them. The lesson here is that software had no control over the interlocks and if Windows/software crashed then no safety issue. If the hardware interlocks were not engaged no matter how many times I sent a command to fire the laser, it would not fire. Safety did not depend on software.

 

Does the hydraulic press here have hardware interlocks that will protect a user in spite of the software? If so the lack of experience may not be a problem. But if the system is relying on software for safety without any hardware,  I would be concerned.


I was more concerned with stuff like "what if the user spams the button?"

Bill
CLD
(Mid-Level minion.)
My support system ensures that I don't look totally incompetent.
Proud to say that I've progressed beyond knowing just enough to be dangerous. I now know enough to know that I have no clue about anything at all.
Humble author of the CLAD Nugget.
0 Kudos
Message 23 of 53
(934 Views)

Yes the hydraullic press have a hardware based system. It will be a two button system. So that user will have to use both hands to operate the system. Secondly I am planning to use a IR sensor to detect anything in the vicnity. So there is an emergency stop button in the hardware of the press. I am planning to use the IR sensor to program in a way that when the user comes near it the stop button is triggered. And system is stopped. 

0 Kudos
Message 24 of 53
(904 Views)

@govindsankar wrote:

Yes the hydraullic press have a hardware based system. It will be a two button system. So that user will have to use both hands to operate the system. Secondly I am planning to use a IR sensor to detect anything in the vicnity. So there is an emergency stop button in the hardware of the press. I am planning to use the IR sensor to program in a way that when the user comes near it the stop button is triggered. And system is stopped. 


Why use software for that? Connect the light curtain to the stop button.

G# - Award winning reference based OOP for LV, for free! - Qestit VIPM GitHub

Qestit Systems
Certified-LabVIEW-Developer
0 Kudos
Message 25 of 53
(881 Views)

Well we are not making any difference to the hydraullic press. We will just use a button to scan the serial code and the hydraullic press will work as usual and afterwards there are buttons to confirm whether the process was successful or not based on visual inspection. So for this I need a button reader, but I understood we need to use a DAQ device to read a button. I am also using the DAQ device to read digital voltage. So for this I am planning on using 

MCC USB-1208FS-Plus/LS/1408FS-Plus Series: Multifunction USB DAQ Devices. 

https://digilent.com/shop/mcc-usb-1208fs-plus-ls-1408fs-plus-series-multifunction-usb-daq-devices/

So as anyone worked with this. Or do you recommend something else. Kindly let me know. Thank you. 

0 Kudos
Message 26 of 53
(850 Views)

@govindsankar wrote:

Well we are not making any difference to the hydraullic press. We will just use a button to scan the serial code and the hydraullic press will work as usual and afterwards there are buttons to confirm whether the process was successful or not based on visual inspection. So for this I need a button reader, but I understood we need to use a DAQ device to read a button. I am also using the DAQ device to read digital voltage. So for this I am planning on using 

MCC USB-1208FS-Plus/LS/1408FS-Plus Series: Multifunction USB DAQ Devices. 

https://digilent.com/shop/mcc-usb-1208fs-plus-ls-1408fs-plus-series-multifunction-usb-daq-devices/

So as anyone worked with this. Or do you recommend something else. Kindly let me know. Thank you. 


I haven't worked with that one, but it seems similar enough to NIs 6001, so it should be plenty for what you're describing.

G# - Award winning reference based OOP for LV, for free! - Qestit VIPM GitHub

Qestit Systems
Certified-LabVIEW-Developer
0 Kudos
Message 27 of 53
(844 Views)

The more info we get from you (and the other posts in the forum), the more interesting it sounds.  Very cool.  🙂

Bill
CLD
(Mid-Level minion.)
My support system ensures that I don't look totally incompetent.
Proud to say that I've progressed beyond knowing just enough to be dangerous. I now know enough to know that I have no clue about anything at all.
Humble author of the CLAD Nugget.
0 Kudos
Message 28 of 53
(824 Views)

Often times process controllers have their own DIO. Does your hydraulic press controller have a button on it?

 

It also sounds like you might be programming the whole thing in LabVIEW, so maybe that's why you need to read a button.

 

A DAQ will definitely work to read a button, but then again, so would a $3 Arduino clone. Safety will need to be implemented somewhere other than the device that reads the button anyway so I wouldn't feel too bad about using something cheap to sense the button press.

 

There are many devices that'll do what you need it to. Any Arduino, Raspberry Pi, Beaglebone, ESP8266 or ESP32, etc will do the trick. They won't be 100% bulletproof but all they're doing is reading a button.

 

Again to emphasize... you need real, actual, hardware-level safety for this anyway, so you MUST plan to have false button presses sensed in some way. Thus, I don't feel like you need a particularly heavy duty button pressing sensor.

0 Kudos
Message 29 of 53
(815 Views)

As I said, we are not making any change to the hydraulic press. There is already safety implemented in the hardware of the hydraulic press. I am not making any changes. I just need to collect the data from the user to say if the hydraulic press has been successfully completed or not, and also in the beginning to scan the device using a scanner. For both these operations, I need buttons and DAQ. So for scan I need one button, then after completion the user tells software whether it is ok or not by pushing one of two push-buttons. So this part is clear to me. I have decided to buy the NI DAQ 6001. But now the confusing task is deciding the push button. So for the DAQ to read the push-button, the push-button gives a 5V signal to the DAQ. But I am confused on where does the 5V come from. Do I need a separate battery power supply to complete the circuit, or are there battery operated push buttons? Kindly let me know. Thank you. 

0 Kudos
Message 30 of 53
(797 Views)