Hi all,

 

I have a cDAQ-9178, with modules NI 9263 and NI 9205. I am trying to read a variable waveform (from a hall effect sensor), do some basic filtering or alterations, and then output that new waveform as fast as physically possible. 

 

I need some help to determine if a) This is possible b) How to do it.

 

I have attatched my VI snippet (relatively new to Labview and these forums so let me know if I did something wrong). I have tried a few dozen alterations to it, and since Im self taught I'm sure there are some glaring mistakes, but I really need help getting this to work at the same time.

0 Kudos
Message 1 of 15
(11,137 Views)

The glaring mistake I see is that you have write task executing at 20 kHz, while the read task is only occurring at 15 kHz.  Seems to me that they should be  the same rate.

 

How simultaneous to you expect or need "simulataneous" to be?  Because of your 100 millisecond metronome in the loop, You will likely have at least a 1/10th second delay from the input to the output.

0 Kudos
Message 2 of 15
(11,111 Views)

Thanks for that, I fixed the rates. I know I cant expect actual "simultaneous" - my arbitrary waveforms will be on the order of 100 to 200 hz, and It is acceptable to have the signal lag behind by a small (less than 5 degree? unsure yet) phase difference. I can lower the metronome in the loop (or remove and place with a tiny wait function).

 

The main problem is simply that I keep getting errors like error -200452, where I can't write since there is an empty buffer. I've tried to add in "configure output buffer", but I can't figure out how to do so and actually have the program output anything. 

0 Kudos
Message 3 of 15
(11,094 Views)

@combo531 wrote:

Thanks for that, I fixed the rates. I know I cant expect actual "simultaneous" - my arbitrary waveforms will be on the order of 100 to 200 hz, and It is acceptable to have the signal lag behind by a small (less than 5 degree? unsure yet) phase difference. I can lower the metronome in the loop (or remove and place with a tiny wait function).

 

The main problem is simply that I keep getting errors like error -200452, where I can't write since there is an empty buffer. I've tried to add in "configure output buffer", but I can't figure out how to do so and actually have the program output anything. 


Time to pull out some tricks:

JJB MOD.png

Where the ugly subvi created from selection is:

Mind boggling hidden control.png

Why did I create that sub.vi?

Capture1.PNG

Inlined!

For something as slow as 20kHz you should be easilly able to achieve that rate unless the UI thread bogs you down updating those charts (You could remove them after tweaking Rank's Value)

 

Rank then sets the delay between In and Out the tradeoffs are Higher rank = better filtering and more delay


"Should be" isn't "Is" -Jay
Message 4 of 15
(11,069 Views)

First, thank you for taking the time to look at this, I have been struggling with this and I greatly appreciate the help.

 

So I took the VI you created and reproduced the SubVI properties like you pointed out and I still run into errors. As your VI was, I run into: 

 

Error -200077 occurred at Property Node DAQmx Timing (arg 2) in DAQmx Timing (Sample Clock).vi:4730004->Stand Alone Optical Drive.vi

Possible reason(s): Requested value is not a supported value for this property. The property value may be invalid because it conflicts with another property.

Property: SampQuant.SampMode
Requested Value: Hardware Timed Single Point
Possible Values: Finite Samples, Continuous Samples

Task Name: _unnamedTask<4>

 

Since it had a problem with Hardware Timed Single Point, I tried changing both to either continuous samples or finite samples but then I run into:


Error -200462 occurred at DAQmx Start Task.vi:7220004

Possible reason(s):

Generation cannot be started because the output buffer is empty.

Write data before starting a buffered generation. The following actions can empty the buffer: changing the size of the buffer, unreserving a task, setting the Regeneration Mode property, changing the Sample Mode, or configuring retriggering.

 

Any thoughts on why these errors occur and how to circumvent them?

 

0 Kudos
Message 5 of 15
(11,060 Views)

Since it had a problem with Hardware Timed Single Point, I tried changing both to either continuous samples or finite samples but then I run into: 

finite samples seams reasonable (Wish that device could go HTSP) for both the AO and AI


Error -200462 occurred at DAQmx Start Task.vi:7220004

Possible reason(s):

Generation cannot be started because the output buffer is empty.

Write data before starting a buffered generation. The following actions can empty the buffer: changing the size of the buffer, unreserving a task, setting the Regeneration Mode property, changing the Sample Mode, or configuring retriggering.

 

Any thoughts on why these errors occur and how to circumvent them?
As a matter of fact I do.  This is obviously the AO task.  Replace the Start Task vi with DAQmx Control Task.vi and wire the input to a "Commit"  That places the task in a state as close to run as possible and will really lower our overhead inside the loop.  It should "Auto-Start" with the Write.vi write one sample and return to the commit state every iteration of the loop. Check here for a great peek at DAQmx State Transitions and Here for the duct-tape-required tour.  

We should rethink the AI task and change it back to Contineous Acquision, sample rate = 20000 and Samples to read =1. Use a read 1ch n samp dbl The loop will pace with the AI having 1 sample available.  Index the first element (there will only be one)  run it through the filter into the AO write.

The trick here is we need to iterate faster than 1/20kSec so that the input buffer does not get a backlog (that will eventually throw another error) So, we need to have that loop doing nothing but DAQmx related stuff.  So, Add a Queue! and queue the Raw and Filtered Doubles up for display elsewhere  Use the trick found here Serendipity rides again of writing to the graph from a "flush queue" to limit the burden on the UI thread Flush it every 200ms or so.

 

You are really digging into my bag of tricks now aren't youSmiley Very Happy

 

 


"Should be" isn't "Is" -Jay
Message 6 of 15
(11,048 Views)

Thank you for your help, you got rid of those errors but now I am running into one more, since I'm not sure If I have implemented your suggestions correctly. I've attatched the VI snippets, does this look right? I'm now running into an error:

 

Error -200609 occurred at Stand Alone Optical Drive.vi

 

Possible reason(s):

Generation cannot be started, because the selected buffer size is too small.

Increase the buffer size.

Selected Buffer Size: 1
Minimum Required Buffer Size: 2

Task Name: _unnamedTask<21>

 

I tried completely removing everything with the Queues (since I haven't worked with them before and I figured that would likely be a source of my mistake), but I still have the same problem. Do I need to add a configure buffer function?

Download All
Message 7 of 15
(11,008 Views)

Actually not half bad!  I'm a bit surprised by that error!  The Wait was the worst of your mistakes.  The DAQmx read will pace the loop.  I fixed your queue datatype.

 

Give this a shot.

Capture.PNG

 

You May need to transpose the 2D array in the display loop.  You'll know if the charts look really odd


"Should be" isn't "Is" -Jay
Message 8 of 15
(10,989 Views)

I think it is almost there, the program would run for a few loop iterations (5 to 10) and would read and output, but it eventually hangs and gives this error:

 

Error -200292 occurred at Stand Alone Optical Drive.vi


Possible reason(s):

Some or all of the samples to write could not be written to the buffer yet. More space will free up as samples currently in the buffer are generated.

To wait for more space to become available, use a longer write timeout. To make the space available sooner, increase the sample rate.

Property: RelativeTo
Corresponding Value: Current Write Position
Property: Offset
Corresponding Value: 0

Task Name: _unnamedTask<39>

 

I tried increasing the rate, and placing a longer timeout but neither really fixed the problem. Then again, I chose arbitrary values for both so maybe that is still a solution

 

0 Kudos
Message 9 of 15
(10,943 Views)

I think it is almost there, the program would run for a few loop iterations (5 to 10) and would read and output, but it eventually hangs and gives this error:

 

Error -200292 occurred at Stand Alone Optical Drive.vi


I was afraid of that (and exactly why I set the output buffer to as low a value as possible.

 

Detailed explaination:  What is happening here is two processes:

 

  1. First we are reading 1 value writing it to the AO output buffer and reading another value and outputing it to the output bufffer... at 20kHz
  2. Asynchronously. the AO task is Transitioning to the run state, reading the output buffer, initiating a D-A Conversion and finally transitioning back to the commited state.  This process is not keeping up with the first process.  Smiley Sad

 

The some might think that increasing the size of the output buffer is the simple solution.  They would be dead wrong!  If the AO task cannot keep up with the AI sample rate the buffer is going to get fuller and fuller and the AI-AO lag will increase as a function of time.

 

Others would suggest using a Wait for Task Complete on the AO Task- They would be wrong too, This just fills the AI Input buffer and you will be reading data that was actually aqcuired some time in the past again, the AI-AO lag will increase as a function of time.

 

We need to do one of two things.

A: Speed up Process 2 (Prefered)

B: Slow Down Process 1

 

B. is easy as pie, lower the sample rate of the AI Task And we will use this as a "Fall-Back" option.  A. should be attempted first.

 

Next Step.  Wait...... I'm coming back with example code

 


"Should be" isn't "Is" -Jay
Message 10 of 15
(10,935 Views)