What filter to apply for a 50 Hz signal
hello All,
We are acquiring input 240V,at 50Hz, 3 phase voltage thru voltage transducer and that is fed to NI Input DAQ card, NI USB 6210 using LabVIEW 2019
When we check in the program, we see that
Rphase is on AI0 channel -> perfectly sinusoidal on the graph
Yphase is on AI1 channel -> skewed
Bphase is on AI2 channel -> skewed
I put low pass filter butterworth order 3, now the waveforms are OK but Y and B phase amplitude has reduced.
What should be done for the correction, please let me know.
attached waveform screenshot here
actual waveform has all 3 phases same amplitude but Y phase, Bphase skewed.
Filtered waveform shows  clear waveform on R, Y B...But Y and B amplitude is lesser than Rph.
All phases connected to 3ph 240V input signal. 3 transducers also OK.
(1,603 Views)
Accepted by hemalathagopal
By the picture my first two guess: voltage transducer maybe a transformer where one phase is also abused as power supply?  (saturation)
or
Depending where you measure and what (bad) powersupplies are hooked on the system ..maybe real signal ?
If you swap channel inputs does the signal shape follow or not?
You use a multiplexed input card. See spec  and Fig 1. All channels have the same (hopefully low) source impedance?
If you hook up a scope (even 2 channel), how does the signals looks like?
Greetings from Germany
Henrik
LV since v3.1
(1,594 Views)
Thanks for the market solution 🙂
Are you willing to share the solution?  (Just curious 😄 )
Henrik
LV since v3.1
(1,510 Views)