07-22-2016 04:00 AM
Hello,
I have a problem with my EtherCAT system.
The system contains:
a PXI-8840 RT
2 Position sensors with EtherCAT
and 8 Inverters with EtherCAT (with Softmotion plugin and xml file)
I'm using LabVIEW 2015 with RT, FPGA and Softmotion modul.
At the beginning of my code I switch the scan engine mode to configuration mode and afterwards to active mode programmatically. This works well when I start my code with LabVIEW, but I receive an error when I use a startup application. The error code is -2132869095 (The deployment connection has timed out). I have tried this also with a code just containing the VIs for switching the scan engine mode and nothing else. With this I receive the same error.
The problem occurs when one or more inverters are in the project.
Has anyone an idea what I have to do to avoid this error?
Thank you.
Solved! Go to Solution.
07-26-2016 06:40 AM
Dear m.kroschk@eaat.de,
this is really a very strange behavior but I found a comparable issue in our internal database which was resolved by reformatting & reinstalling software to the RT-System.
So first of all I would ask you to try reformatting & reinstalling software your PXI-Target.
If the Error still appear, please Zip and post your minimum project for reproduction which I could test here to reproduce the issue on my system.
Kind Regards,
SG3 | Staff Applications Engineering | National Instruments | NIG |
07-28-2016 04:58 AM
Dear SG3,
thank you for your reply. Reformatting and reinstalling the software don't fix the error. But I found two articels, which may help me:
http://digital.ni.com/public.nsf/allkb/0C20921D7960CBF286257F42005EC033
http://digital.ni.com/public.nsf/allkb/E2F4F2E4F3A91F6E86257BB9006589D1
I will try this and give you an information.
Thank you
07-29-2016 02:40 AM
Hello,
the two articels mentioned in my last post have fixed the problem. I have to follow this exact sequence and I have to wait until the scan engine is running.
Now, my startup application is running.