pid output
i'm having problems with my pid in the sense that it only outputs 2 values(min and max).i've tried different gains and still, it will not operate properly.can anyone help me please? the process i'm tring to control is a oven, and i am using NI 6024E and SCC-2345.(i also tried without the dt s, by using a simple wait in the while loop, but it doesn't influence the it)
(3,198 Views)
Accepted by topic author Gixxerash
Your output range is tiny (0 to 0.02).  Meanwhile your input appears to be on a much larger range.  Since your P gain is 20, any error (difference between setpoint and process variable) greater than 0.001 is going to be enough to drive the output either full on or full off (20 * 0.001 = 0.02).  You either need a larger output range (and then rescale before sending the output to the DAQ device) or much, much smaller gains (which could result in the loss of some mathematical precision).
(3,190 Views)
thank you, it seems to do the trick. thank you
(3,180 Views)
