"Read Tag" to slow

Hi...
I'm using the "Read Tag.vi" from the DSC module to read the tag from an OPC server.
The "Read Tag.vi" is placed in a loop so it should run al the time and i think a have managed to set the deadband for the tag to 0 in the "Tag configuration editor". The tag is a value from 0 to 32000, and i'm measuring a temperature, so the measuring changes all the time. 
The problem is that it is not reading the tag unless the tag value changes a specific amount. I thought that it was the deadband, but it's not it. When i use another client it works fine and it update all the time.
 
Thanks.
 
Carsten Toft
Aalborg University Esbjerg, DK

Message Edited by Toft on 11-10-2005 12:13 PM

0 Kudos
Message 1 of 3
(2,697 Views)
There is a deadband in two places. One for the tag and one for the I/O group. Double click on a tag. Go to the Connection tab. Press the Edit button under the I/O group name. Set the deadband value on the popup window to 0.
0 Kudos
Message 2 of 3
(2,686 Views)

Thank you, that was the problem. Now it works perfect.

Carsten Toft
Aalborg University Esbjerg, DK
0 Kudos