We found this problem only on some machines. So, a quick resolution would be to try some other make of computer (at least one with a different motherboard).
After a lot of trouble-shooting we reached the conclusion that the incompatibility will come up most frequently with this particular combination:
Scan-Data Bell 202 modem + Lookout's serial routines + certain UARTs on certain motherboards.
Scan-Data can say that it is not their problem, since it doesn't happen with other software. However, an interesting note - we were also able to replicate the lack of communication from the UART with PortMon, which is a third-party freeware tool. So, we think that there is something
unusual about the way the RTUs' modems communicate with that type of UART and Lookout is more sensitive to this situation.
After changing values for RTS, CTS, timeouts and other comm. parameters, we decided to try one of NI's serial cards. It worked. I am not suggesting you buy NI's serial card.. but that's what we did.
Disclaimer: Though your problems sounds similar.. it could something else.. so please don't hold me for anything!
Hope this helps.
Regards,
Khalid