Kevin,
The way I have handled the AC PWR FAIL at the RTU is to wire up a 120 VAC ice cube relay to the incoming power (before the UPS) and wire the contact (NO or NC) to a DI of your Zetron. This way, you will know if you have an AC PWR FAIL at the RTU. While there is AC, the coil of the relay will be energized. If the AC goes away the coil will de-energize and OPEN or CLOSE (depending how you wire it up) your contact, sending a signal to the Zetron giving you enough time to log the Alarm in Lookout.
As far as shutting down Lookout, I don't have an answer for you.