I can't figure out how to change a PC address connection on a button

I'm a new user of Lookout. I'm working on an existing application. I can see PLC connections on analog entry and display items, but I don't see how to look at and alter the connection of pushbuttons. They all seem to be local but i know from looking at the PLC program that they are connected to the PLC address. I'm feeling kind of stupid.

0 Kudos
Message 1 of 3
(4,872 Views)

If they are local, you will need to find the driver object, right click and clock Edit Connections, then find the connection.

 

Another way find the connection is to use the Connection Browser, under Objects.

 

Good luck!

-----------------------------------------------------------------------
Forshock - Consult.Develop.Solve.
0 Kudos
Message 2 of 3
(4,812 Views)

Got it. Thanks. I was looking at the connection backwards by looking at te connection of pushbuttons rather than the connection of the tag.