IA OPC 5.1 Causing a backplane comm error w/ GE PLC 90-30 374+ CPU

Hello,

 

So here is what's going on. I have a Series 90-30 Setup W/ a high capacity p/s and a 374+ CPU. I am trying to find the correct configuration of communication to replace the 364 CPU which is now obsolete. I read the notice thoroughly and to my understanding the 374+ with a rev of at least K (or something like that) and a high capacity p/s should be the direct replacement. Now I can connect via serial no problem. But when trying to connect via ethernet for Industrial Automation OPC 5.1 I receive a configure connection error as well as a system fault on the plc "backplane communications with PLC fault:lost request"

 

any ideas?

 

-Jason 

0 Kudos
Message 1 of 3
(6,591 Views)

http://digital.ni.com/public.nsf/allkb/0A10A59F90CCF124862570A00055CBE5?OpenDocument

 

It cannot work with 374 via Ethernet...

Ryan Shi
National Instruments
0 Kudos
Message 2 of 3
(6,576 Views)

if you need to comunicate With 374 or 372 cpu with lookout driver if possible by GE versamax ethernet driver

the problem is the limit of register to %r02048

 

The protocol for ic200cpuE05 is like the 37x 90.30 cpu