Lookout 6.5 clients not connecting to server

I am having problems with some clients in that they do not reconnect trace data automatically when a server goes off and back on line.  The client Lookout application needs to be restarted for traces to come back.  I'm still looking into this, however I have seen the behavior inconsistently with both 6.2 (more consistently) and 6.5 clients.  This problem also existed rarely before upgrade to 6.5 server with 6.2 server/client.

0 Kudos
Message 31 of 38
(4,048 Views)

I am notified occasionally by some client users that they have no trends after I have restarted the server, and I have to stop and restart the nicitdl5 and lkads services as well as closing and reopening lookout on the client machine. I suspect it happens more but I assume my client users are rebooting their computers without notifying me which corrects the problem. And this does not happen on all of my clients after server restarts - random occurrences.

Jason Phillips
0 Kudos
Message 32 of 38
(4,042 Views)

The reconnect problem looks like a bug in citadel or logos. I will try to replicate it on our test machines.

Ryan Shi
National Instruments
0 Kudos
Message 33 of 38
(4,032 Views)

I am seeing the same problems, I have installed v6.5 on my servers and as I am going around to my clients, I install the software on the client machine and Lookout freezes up on both redundant servers, and I have to restart both servers.

MWarner
0 Kudos
Message 34 of 38
(3,926 Views)

I created the Logos folder and that corrected my client and server software not responding issues.  Now I cannon see the alarms from the server on the client.  I went into Alarms/Select Process clicked on network to expand it, but the hour glass just comes up and nothing happens.  I tried registering the server computer and it says computer already registered.  I also opened Tag Monitor, tryed connecting to the network computers and it cannot connect either.  I am using a Laptop Compaq 1.40ghz running xp sp3.

MWarner
0 Kudos
Message 35 of 38
(3,912 Views)

If the Tag Monitor doesn't work, the problem is in the Logos communication. Make sure the necessary ports have been opened for Logos.

http://digital.ni.com/public.nsf/websearch/8AE45BBFA1D7025E862570F200642FD8?OpenDocument

Ryan Shi
National Instruments
0 Kudos
Message 36 of 38
(3,890 Views)

Hi Ryan,

 

Any luck with this Hypertrend data reconnect bug issue?

 

Ed

0 Kudos
Message 37 of 38
(3,661 Views)

Looks like I'll be reading alot to stay up to speedSmiley Surprised

0 Kudos
Message 38 of 38