Modbus refreshing tag, automatic update of values

Hi,

 

I need your help concerning a problem on lookout 6.0.2 with many Modbus
object.

I’ve done many tags on this object who are reading different value on an
Adams-4018+ and Adam-4017+.

 

When I open the programme they are read correctly one time. After, no
automatic
refreshing of the tags is done.

I’ve put a value in the parameter “pollrate” of each modbus object = 0.1

I use the modbus serial protocol and every modbus object got is own unique
address on the good comm. Port.

 

Can you tell me why it’s not working and how to do it refresh automatically
at
the fastest possible rate (0.5 sec would be ok)

 

Thanks,

 

Alexandre Bolduc Ing.jr

0 Kudos
Message 1 of 3
(5,982 Views)
Lookout is based on days; an integer value of 1 would be 1 day.  The value of 0.1 is one tenth of day which makes your polling rate once every 2.4 hours.  If you want to specify seconds, use a time format that includes colons such as 00:00.5 (every half second) or 1:00 (every minute).
0 Kudos
Message 2 of 3
(5,980 Views)

Thanks a lot!!

it<s exactly that!

 

AleXxX