I am having a nuisance problem with "red X".  I am running Lookout 6.0.2.  I am using PLCDirect DL205 series PLC processors and H2-ECOM100 Ethernet modules.  Lookout and PLCs are connected via Ethernet radios.  These radios connect at 256 KB, which I realize is slow, but this is what I have.  Lookout connects fine to all devices, and we have not had any comm link become disabled during normal operation.
 
This setup looses packets on occasion (more often than I would like).  This generates a "Transport Protocol Error" in the alarm screen each time it happens, and the dreaded "red x" for one to two seconds.  The second retry is good 99.99% of the time, and the alarm clears.  I have spoke with NI and AutomationDirect several times to change timeout settings, poll times, etc.
 
I am going to generate a "heartbeat" in the PLC for monitoring of an actual comm failure, and I would like to disable the "red X" on the displays.  Can this be done?
 
I tried replacing the "red x" graphic with a very small box, but this did not work.
 
 
0 Kudos
Message 1 of 2
(3,319 Views)
i get the red x's every once in awhile on one of my systems even after doing all the latest firmware upgrades on the ecom100...although i am not using radios....it used to happen several times a week but it just happens maybe once every other month or so now....you might make sure you have the latest firmware on your ecom....thanks...randy