There are a couple of things you should consider while connecting the 7342 to the ES-22BS. First of all, make sure that the inhibit output signal of the 7342 has been configured for active high polarity in the UMI-7764 using the switches provided in the interface. Second, both the inhibit outout (which will go to the shutdown input on the ES-22BS) as well as the step and directio outputs on the 7342 are open collector or current sinking outputs. Since your drive's step, direction and shutdown signals are all optically isolated and thus require powering an optocoupler to work, then the current that they would require might be higher that what our outputs can generate. The proper way to connect optically isolated signals to the 7342 would be to use a +5v power supply
capable of sourcing the 6.5 mA minimum current required by your input lines (usually the same supply that you use to power the UMI) and connecting the +5v to the plus terminal of each of the signals (namely step+, direction+ and shutdown+). Then you will take each of the command signals form the 7342 and connect them to the respective minus inputs on the drive, so your connection diagram should be something like this:
- UMI7764 ES-22BS
- Step+ -> +5v
- Step -> Step-
- Direction+ -> +5v
- Direction -> Direction-
- Shutdown+ -> +5v
- INHOUT -> Shutdown-
Since an open collector ouptut only has two states, either active low or floating, this scheme will allow your drive to see an active high signal when the output is low and an active low signal when the output ges into the floating state because the 7342 folats to +5v thorough an internal 3.
3K pullup resistor.