How can I control a burkert valve 3280 by LabView?
I would like to know how to control a burkert valve
3280 H 8.0 FKM MS
G1/2 PN 6bar
24V C 12W
The valve is connected to a condenser, and I want to control it according to the outlet temperature by using NI 9474?
Message 1 of 8
(1,734 Views)
NI 9474 is a switching card.
Your value is type "H," which means it needs a signal to represent the position as per the user manual.
For a Control value, the standard signal has to be one of the 4-20mA or 0-5V or PWM
So you need a different c-series card to control the 3280 value from LabVIEW or any language using the cDAQ.
DIP switch within the housing configure whether it responds to 0-5V signal or 4-20mA signal.
Santhosh
Soliton Technologies
Message 2 of 8
(1,714 Views)
Thanks for this info. I already run the valve by using two power supplies: 24V and 0-10V to control the opening area.
It seems to me that the DIP switch set to Set-point value input 0...10 V by default.
To control it by LabView, I think I need a module generating voltage instead of using adjustable power supply like I did to implement the electrical connection shown in the attached table. My questions is which model ("c-series card") in specific I could use?
Message 3 of 8
(1,695 Views)
OK.
I used NI 9269, and it perfectly works. Now, how can I adjust the opening area (control the valve) according to a temperature measurement?
Message 4 of 8
(1,680 Views)
@alhabeeb wrote:
OK.
If you're trying to maintain a temperature set point by adjusting the valve, you should probably adopt a PID control algorithm.
But, in general, you need to come up with the logic or map a temperature value to an equivalent value position value.
Santhosh
Message 5 of 8
(1,674 Views)
Yes I should use PID control. May I have additional explanations about it? Is it required to read the output signal form pin 7?
Message 6 of 8
(1,665 Views)
Any reason you need to implement this process control in LV instead of a dedicated PID controller?
Based on the manual, Pin 7 seem to represent the end position limit switch,
Santhosh
Message 7 of 8
(1,654 Views)
Because I have to use LabView.
Message 8 of 8
(1,650 Views)
