Using Analog Input from M-Series DAQ card for Feedback in motion controller PCI-7350 Card
Hi, I have an analogue input from SC-2345 into M-series DAQ card. Now, I wish to configure this analogue input as analogue feedback in the motion controller PCI-7350 card. I am not able to use the analogue input in PCI-7350 as it requires an additional SCB-68 and it will create some noise problems. Is it possible to to use analogue input from the DAQ instead?
(3,427 Views)
Hi yanxinix,
the analog feedback is part of the real-time loop running on the PCI-7350. If you acquire the analog signal with an M-Series device this would mean, that you have to transfer the acquired signal to the PCI-7350 via the PCI bus. This requires software interaction on the PC and a significant delay and jitter caused by the low-priority host communication process on the PCI-7350.
Besides the fact that the PCI-7350 doesn't accept feedback signals from the PCI-bus anyway, the process described would add a feedback delay of about 5 to 10 ms and a high amount of jitter, making stable control behavior impossible.
So I'm afraid, this approach is not feasible. If you want to use analog feedback with a PCI-7350 you have to use the analog inputs on this board.
Kind regards,
Jochen Klier
(3,426 Views)
