Books on Standard Grounding or noise reduction principles?

Hello everybody,
 
I have heard that there are certain websites where if you register they send certain books on Standard Grounding Principles or on Noise reduction techniques. I have recently started working with Data Acquisition Systems as a student and am facing a lot of noise problems. Can someone point me toward those websites or suggest some good text in this area.
 
Thanking you.
Viku.
0 Kudos
Message 1 of 5
(3,942 Views)
Have you tried searching this site? There are a lot of aritcles related to such topics, especially how they relate to data acquisition.
~~~~~~~~~~~~~~~~~~~~~~~~~~
"It’s the questions that drive us.”
~~~~~~~~~~~~~~~~~~~~~~~~~~
0 Kudos
Message 2 of 5
(3,937 Views)
My favorite book on the topic is

Grounding and Shielding Techniques in Instrumentation by Ralph Morrison

It is exhaustive on the topic....

When I first got the book I overheard one of my colleagues saying to a graduate student, "... and the amazing thing is, he actually *reads* that stuff".
John Weeks

WaveMetrics, Inc.
Phone (503) 620-3001
Fax (503) 620-6754
www.wavemetrics.com
0 Kudos
Message 3 of 5
(3,936 Views)
FYI - Here is a great tutorial on Field Wiring and Noise Considerations.  This has been very useful for me in the past!
-Alan A.
0 Kudos
Message 4 of 5
(3,921 Views)

Hello everyone,

 

I would like to have your advice for a specific issue. I could not decide on whom to discuss with, but I believe that your experiences may help me on the subject. I am designing a DAQ system with PCI-6123 cards.

 

I work on power electronics and power systems. I usually have to deal with racks, cablings, controller card designs, PCB implementations which are in fact do not seem to be directly related to my area, but they are. We usually have EMI and coupled noise problems in our circuits.

 

My confusion is about shielding and grounding. By this, I mean,

 

1) Where the shield conductor of a shielded twisted pair cable should be connected? Should it be Earthed, or should it be connected to the reference voltage point of the signal generator?

 

2) How should a metal enclosure covering a PCB employed? Should it be connected to Earth or analog ground of the PCB?

 

 

I have read thorough lots of documents and books, but the subject is still not clear. In “Noise Reduction Techniques in Electronic Systems” of Henry W. Ott and “Grounding and Shielding Techniques in Instrumentation” of Ralph Morrison, the causes of noise and interference are covered in detail and are well understandable. Shielding against magnetic interference (twisted pair or coax cable, steel enclosure rather than aluminum or copper, etc.) is also clear. However, shielding against electric fields (electrostatic effects) is rather confusing. It is mentioned to connect the shield of a cable to the ground. The word “ground” means so many things. Is it the Earth, or the reference voltage point of the DAQ (measurement) system, or the reference voltage point of the signal generator (or power supply)? This is not clear.

 

In an application note by Alan Rich of Analog Devices it says: “An electrostatic shield, to be effective, should be connected to the reference potential of any circuitry contained within the shield. If the signal is earthed or grounded (i.e. connected to a metal chassis or frame, and/or to earth) the shield must be earthed or grounded. But grounding the shield is useless if the signal is not grounded.” The schematic is given (please see the attachment) and it is said that D is the best solution because no noise voltage can be coupled to V12.

 

 

This paragraph is very clear indeed. However, we have purchased some equipment whose input and output connections are made with all shielded cables. The manufacturer recommends that the whole equipment should be placed in a 19” rack, the rack should be well earthed, the equipment chassis should be well connected to the rack (thus to earth) and all the shields of the cables that go outside of the rack should be connected to earth (rack earth bar) also. This sounds reasonable if 1) All the signals are generated by the equipment inside the rack, 2) The reference voltage point of all the signals is the Earth. I found out that, the first one is true, however the other is not. Because I know that the signals are isolated from each other. This violates that there exist only one reference voltage point. So, what does shielding do good for?

 

So the question arises: Are there any different situations that I should connect a metal enclosure of electronic equipment to Earth, and all the shields to Earth, although the signals are not referenced to Earth? By the way, some of my colleagues strictly argue that all the shields and enclosures should be earthed no matter the signal inside is earthed or not, depending on their experiences, but I am not satisfied with their explanations. Does this method solve problems of RF or other interferences created by broadcast antennas, 50/60 Hz power lines, lightnings, contactor switchings etc.? Or does Alan Rich’s paragraph cover and take into account these interferences and should I be sure?

 

I will appreciate your help very much. Looking forward to your reply.

 

Best Regards,

 

Cem Özgür