How to control SSRs using NI9264?
Hi, all
I want to control 18 SSRs (CSW-2410) using 2 units of NI-9264.
But, I could not output voltage correctly. For example, measured voltage is about 2.8V even though I connect NI-9264 to SSR and set 10V.
This is final problem I have. Does anyone have a good idea?
(2,694 Views)
Typical input current is ~10mA for the SSR:
https://www.mouser.com/ds/2/657/c_s-1063282.pdf
The 9264 output current is limited to ~4mA typical, it is unable to drive the SSR and thus why you may be seeing a reduced voltage output- it is overloaded.
http://www.ni.com/pdf/manuals/378025a_02.pdf
-AK2DM
(2,678 Views)
add a transistor as a voltage follower or open collector
and add a 12V powersupply
or use a DIO card that can drive the current...
Greetings from Germany
Henrik
LV since v3.1
(2,636 Views)