How to read pressure in real units (e.g bar) from input analogue voltage?
Hi
I have 35 X HTT Pressure Transmitter (3 wires) and NI-9205 which acquires the reading of the pressure sensor 35 X HTT as voltage. How can I convert it to bar for example?
Message 1 of 8
(1,517 Views)
According to this data sheet, the sensor has a range of 0 to 1 Bar and an output voltage range of 0 to 10V.  This makes the math easy: just divide by 10.
Message 2 of 8
(1,501 Views)
So, Is it always a linear relationship? If my sensor ranges 0 to 30 bar, first divided by 10 then multiply by 30?
Message 3 of 8
(1,477 Views)
Unless told otherwise in a datasheet, assume linear relationship.  Because the min of both the voltage and measurement, it is a simple 30Bar/10V = 3Bar/V.
Message 4 of 8
(1,468 Views)
In the datasheet:
But I didn't understand it.
Message 5 of 8
(1,464 Views)
@alhabeeb wrote:
In the datasheet:
These are about the internal working of the transmitter and do not care in the context of the electrical equivalents.
Treat the output signal as linear mapping to the pressure measurement range.
Santhosh
Soliton Technologies
Message 6 of 8
(1,451 Views)
Thanks for your response.
As you said, I should have 0.333333 (V) when I measure the ambient pressure, Should I?
I'm using ni-9205 to aquaire the out signal. I connected pin 1 and pin 3 to negative and positive, respectively to the power supply 23 (V), and I connected pin 2 to channale 0 of the ni-9205 and the negative terminal from the power supply to COM of the ni-9205 and I used differential configuration, but I got not logic voltage readings (e.g. -0.4)!
Any suggestion to solve this issue?
The photos of my devices are shown here
alhabeeb_0-1721989265913.jpegalhabeeb_1-1721989283237.jpegalhabeeb_2-1721989296491.jpeg
Message 7 of 8
(1,428 Views)
Approximately 0.33V for 1 bar pressure.
Were you able to confirm the sensor outputs 0.33V using a multimeter?
In addition, please connect the AISENSE to COM on 9205 terminals.
Santhosh
Message 8 of 8