How to wire pressure sensor PR-35XHTT with ni-9205
I'm using ni-9205 to aquaire the out signal. I connected pin 1 and pin 3 to negative and positive, respectively to the power supply 23 (V), and I connected pin 2 to channale 0 of the ni-9205 and the same negative terminal from the power supply to COM of the ni-9205 and I used differential configuration, but I got not logic voltage readings (e.g. -0.4)!
Any suggestion to solve this issue?
The photos of my devices are shown here
Message 1 of 8
(1,410 Views)
If you are using DIFF terminal mode, the GND pin should be connected to AI8
Reference: NI-9205 Getting Started
https://tmesystems.net/
Message 2 of 8
(1,385 Views)
How about the COM?
Message 3 of 8
(1,332 Views)
OK. I tried (RES) connecting as shown in picture
but I got 0.00771544 (v) as shown in picture below! It is supposed to be 0.3125 (v) as long as I measure the ambient pressure which 1 (bar)
Message 4 of 8
(1,324 Views)
Please cross check the voltage across pin2 and pin1 using a handheld multimeter to ensure the pressure sensor is working.
Santhosh
Soliton Technologies
Message 5 of 8
(1,313 Views)
I think it is not good to measure the ambient pressure.
Message 6 of 8
(1,308 Views)
Accepted by topic author alhabeeb
It is possible, best to test with a pressure chamber or at least compressed air blowing on the sensor.
Santhosh
Message 7 of 8
(1,304 Views)
Yes, it works with a water pump.
Message 8 of 8
(1,296 Views)
