Hi NoraLa,
The Multifunction DAQ devices contain onboard programmable Gain Instrumentation Amplifiers to amplify or attenuate signals before interfacing with the ADC in order to maximize the resolution capabilities of your board. If you set the minimum and maximum of your range to correspond to your sensor, DAQmx will set the PGIA to the appropriate gain setting. For your board, this will be the -500mV to 500mV range. Since your board also has a -50mV to 50mV range and your sensor varies between 0-100mV, depending on the connection type (differential vs. RSE, how many wires you have coming from your pressure transducer) you may be able to use this higher gain setting