PCI 6251 analog input error
I installed PCI 6251 in my newly purchased PC. The PCI card is providing 10.5 V (Attached test panel output for reference) in all analog input channels without connecting any input to connecting board. Clarification in this regard will be helpful.
Thanks in advance.
(1,374 Views)
Any measurement with the analog inputs floating is not valid. Please try connecting the analog inputs to a known signal or ground and verify the measurement.
Read more here - https://knowledge.ni.com/KnowledgeArticleDetails?id=kA00Z000000P6TeSAK
Santhosh
Soliton Technologies
(1,357 Views)
Thank you so much for your clarification. In my case after connecting 5V external supply to Analog input in both Differential and RSE mode also reading the same voltage of 10.5 V. If i change the range to +/-5 then it reads 5.3V. Analog input seems to read the maximum voltage as saturation.
Thanks in advance.
(1,341 Views)
Accepted by topic author cmvragavan
This seems to be a case of saturated ADC measurements since you tried with an external known voltage source, as the last attempt, please try grounding the AI terminals to AGND and observe if you see close to 0V, if you still observe close to range max, then it is a sign of damaged card and you need to have it repaired or replaced.
Santhosh
(1,323 Views)
