02-19-2007 03:22 PM
02-20-2007 12:55 PM - edited 02-20-2007 12:55 PM
If your acquisition is finite (sample mode on
the Timing function/VI set to Finite Samples), NI-
DAQmx allocates a buffer equal in size to the
value of the samples per channel attribute/property. For
example, if you specify samples per channel of 1,000 samples and your
application uses two channels, the buffer size would be 2,000 samples. Thus, the buffer
is exactly big enough to hold all the samples you want to acquire.
If the acquisition is continuous (sample mode on the Timing function/VI set to Continuous Samples), NI-DAQmx allocates a buffer equal in size to the value of the samples per channel attribute/property, unless that value is less than the value listed in the following table. If the value of the samples per channel attribute/property is less than the value in the table, NI-DAQmx uses the value in the table.
| Sample Rate | Buffer Size |
| no rate specified | 10 kS |
| 0–100 S/s | 1 kS |
| 100–10,000 S/s | 10 kS |
| 10,000–1,000,000 S/s | 100 kS |
| >1,000,000 S/s | 1 MS |
You can override the default buffer size by calling the Input Buffer Config function/VI.
Message Edited by David S. on 02-20-2007 01:01 PM