04-01-2020 01:10 PM
I have a NI cDAQ-9189 chassis with a NI-9996 module in slot 1, NI-9403 in slot 2, NI-9228 in slot 3, and a NI-9870 in slot 4. NI-Max says there is a compatibility issue with the slot 4 module. Looking on-line it seems the NI-9870 RS232 module is not compatible with cDAQ but it is with cRIO. Is this true? To make things worse, I don't see any RS232 modules for the cDAQ chassis. I need to have at least 4 RS232 ports. Is there a 4 port RS2323 module for the cDAQ? Is there one that has the pinout as the NI-9870?
Thanks,
Greg
04-01-2020 01:31 PM
@Greg123 wrote:
Looking on-line it seems the NI-9870 RS232 module is not compatible with cDAQ but it is with cRIO. Is this true?
Yes, that is true. cDAQ only works with modules that can be controlled with DAQmx. RS-232 is not in that realm. If USB is allowed, I would use a ICUSB2324I from StarTech. It is a 4 port RS-232 hub. I have used it quite a bit in the last couple of years with little to no issues.
04-01-2020 01:36 PM
You might try the cDAQ ethernet port connected to a 4 Port RS-232 gateway.