NI Ürünleri İle İlgili Tartışmalar
Comsoft Configurator II Siemens Telegram setting online communication via PROFI
Dear Comsoft.
We bought PCI-Profi from NI, and now try to connect with Siemens Sinamics, but there is problem, so we sending problem report to you.
First, please see the pictures below. These modules & motor are what we are using currently now.
SINAMICS are connected by PC via two different ways. One is by LAN, another one is Profi-bus. We are using LAN for check all connections between SINAMICS controllers & Siemens motor.
PCI-Profi is connected with CU320-2 DP module.
Active Line Module is 6SL3130-7TE23-6AA3.
Single Motor Module is 6SL3120-1TE26-0AA3.
Sensor Module is SMC20: 6SL3055-0AA00-5BA3.
MOTOR MODEL: 1PH8105-1MM20-0LC1-Z.
Active Interface Module 36KW: 6SL3100-0BE23-6AB0.
To check all the functionality is OK, we set the Siemens STARTER like picture above.
Press the online, we only set the “Telegram” for Servo_03” object only: Standard telegram 1, PZD-2/2.
Drives >> Servo_03 >> Commissioning >> Control panel.
We enable all the functions, and give the command to rotate as 60 rpm, and it works good.
We opened “Comsoft Configurator II” to check the PROFI-comm, and set the system like above.
We set “DF_PROFI 2” as Master & Bus address as “1”, and “SINAMICS S120/S150 V4.7” as Slave & Bus address as “3”.
When we make it ONLINE, you can see the GREEN border line.
Now we try to communicate with each other, we opened STARTER, S120_CU320_2_DP >> Communication >> Telegram configuration, then you can see the telegram connection is OK through the “Receive direction” column as shown above.
We opened “Online” debugger from comsoft configurator, and set as like above to activate motor controller.
As you can see, it seems OK. All parameter sent from the configurator was set on Sinamics.
Now turn on “p840[0], BI: ON / OFF (OFF1)” signal, then motor have to be run.
But when we give the parameter like above, we encounter FAULT message: 7840: Drive: Infeed operation missing
So we try to ADD infeed telegram like above: “SIEMENS telegram 370, PZD-1/1”.
In here, we need to FOCUS that all Drive objects have Object number & module number.
Infeed module’s object number is “2”, and module number is “2”, while Servo controller’s object number is “1” and module number is “3”.
We set as same way in “Comsoft Configurator II” like above, and downloaded.
But from the Siemens STARTER, you can see Infeed module cannot connect to Comsoft PROFI-bus: No telegram.
Now, my questions are
  1. Is there something that we are missing?
  2. From Siemens PLC engineer that we heard is, when they are send the command through the telegram, they are set “Object Number” for each module. But it seems, comsoft PCI-Profi configurator only can set the parameter address number. Not the module number. How we can send each module with each command?
Please kindly & fast reply.
Thank you!
Regards
Bryan
BURKE E. PORTER
BEP KOREA T.D.C
Web: www.bepco.com, Email: bryan.yun@bepco.com
Bryan Yun
Engineering Division Control Design Dept. Senior Manager
Address: C-dong 1107, woolimlions valley, 168, Gasan Digital 1-ro, Geumcheon-gu, Seoul, 08507, Korea, Republic of
TEL: 82 2 2026 2592, FAX: 82 2 2026 2589
(7,420 Views)
Seems you are not at the right forums Smiley Very Happy
(7,411 Views)
This is NI recommended Forum category. If it's not the right one, NI have to develope automatic category recommend system 😛
I SEARCHED what I want, but there is none, so they put my question into this forum. So what's the point?
BURKE E. PORTER
BEP KOREA T.D.C
Bryan Yun
(7,401 Views)
This is a local forum of NI (Turkish forums) and consists of Labview and NI hardware sharings (especially Labview) Smiley Wink
(7,391 Views)
Anyway, I solved my problem.
But there is one question with COMSOFT software - you know, COMSOFT PROFI bus is LINKED with NI VISA PXI like shown below.
I just wonder that you used this device before, but it is NI PRODUCT NOW.
And that comsoft provide "configurator" like MAX, on SIEMENS module, in same SLAVE number, they have different kind of modules installed.
for example, on slave 3, they have controller, infeed module(power supply), servo controller, ... etc.
In this case, normally Siemens PLC can SET the module number when they are communicating, but in the comsoft configurator, they don't have.
Only slave number they can set.
So the Siemens speciallist told me, if we want to use several modules on same slave number, we need to give OFFSET for command address for each module.
for example, module1 starts with address 0.
but from module2, we need to multiply 1024, so it starts with address 1024.
module3 start with address 2048, ... etc.
BUT configurator also cannot change the address offset like shown below.
it's disabled to be change.
BEFORE you answer my question, I think the one who USED this device should answer my question.
BURKE E. PORTER
BEP KOREA T.D.C
Bryan Yun
(7,381 Views)
Hello;
As Zafer mentioned this is NI's forum for Turkish speaking customers, not related with Comsoft products.
Also it is not correct stating that "Comsoft products are NI PRODUCTs NOW". They are selling their products from various channels including NI.
I believe you may already noticed that the software you are trying to configure has nothing related with NI products.
Still hope you'll find a solution for your problem somehow.
Thanks.
(Bay) Candan CANER
National Instruments Türkiye
(7,354 Views)
