4...20 mA measurement using PXIe-4302 and TB-4302C

Dear all, 

 

I'm planning to measure multiple analog current signals from different transducer using the PXIe-4302 with the TB-4302C. I found the pictures below in the two manuals of the devices but still confused regarding the wiring. 

e.g inlet 0 and a loop powered transducer

- VSUP = 24 VDC

- AI0 = Sensor power supply???

- AI0+ = Sensor output???

- AI0- = ???

- AI GND = GND (Common for Port 0...3)

- AI Sense = GND (Common for Port 0...3)

Can someone support me in the question? As well as how to change the wiring for a three-wired current transducer. What is the external bias resistor for and do i have to integrate one?

Steve_21_0-1644505490155.png

Steve_21_1-1644505542772.png

 

Thank you

 

Best,
Stephan

 

 

0 Kudos
Message 1 of 3
(2,266 Views)

Can somebody suggest the external bias resister value

0 Kudos
Message 2 of 3
(2,071 Views)

Hi,

 

@Steve_21: Can you make it more clear what your questions are ? Now it seems that everything is a question !!

 

@kanvas: A typical value is 250Ohm for the whole loop. Normal range is from ~50 - 500 Ohm. But typical used values are 50 and 250 Ohm. The 250Ohm is also used to support HART communication.

 

Kees

0 Kudos
Message 3 of 3