Hello,
Thanks for the response! I finally found an Omega current signal analyzer - fancy current driver. I get the same thing happening - it happens in about a minute on the test panel - I forgot to point out in VI logger I had it set for about 10 minutes for the log time.. The voltage is at a steady 3V on the test panel and then starts cycling up to a 10VDC max - there is only 3V present all the time. It still resets after cycling the power.
Thanks,
Eric
08-23-2006 04:15 PM
Hi Eric,
You may check that you are using a proper terminal configuration (differential, RSE, NRSE) for your source. Depending on the type of source, floating or grounded, you may need to add bias resistors. You can read more about this in the Field Wiring and Noise Considerations for Analog Signals tutorial. The behavior you are reporting makes me think that maybe you are missing a bias resistor in your setup or are introducing a ground loop, both topics which are covered in that tutorial.
Please take a look and let us know if you are still having trouble.
Regards,
Laura