01-18-2024 08:43 AM
hi team,
using the NI-MAX I'm installing the software in cRIO 9030 and I'm getting this king for error . and its not installing the software.
I'm also deploying the image file using the RAD utility tool, and I'm also getting some errors, which are below.
Model Model Code Serial Number MAC Address IP Address Host Name App Image Name App Image Version Time Result
cRIO-9030 7755 020BB3EF 00:80:2F:35:8B:C9 192.168.50.173 NI-cRIO-9030-020BB3EF cRIO9030SoftwareImage 1.0.6 0% Error -2147220323 at nisyscfg.lvlib:Set System Image (Folder).vi:2060001<APPEND>
<b>Complete call chain:</b>
nisyscfg.lvlib:Set System Image (Folder).vi:2060001
nisyscfg.lvlib:Set System Image (File).vi:4160001
rad_Deploy Image Wrapper_FB.vi:2760002
can any one help me with this both error
thanks you
01-19-2024 10:08 AM
Hello!
You will need to connect the cRIO to your computer or network using the RJ-45 Ethernet Port 1, as well as set your computer’s IP address to something on the same subnet as the cRIO. If the IP address of the cRIO is 192.168.50.173 Subnet Mask 255.255.255.0, then you will need to set your computer’s IP address to 192.168.50.x Subnet Mask 255.255.255.0. When the status is “Connected running” you can install your software to the cRIO.
Make sure you have installed the LabVIEW Real-Time and FPGA modules. NI recommends using the same version of all software, for example, Labview 2023, Realtime 2023, FPGA 2023, DAQmx 23- installed in that order.
Here is a link to the cRIO-9030 Manual.
Hope this helps!