Signal Conditioning
NI 9217 with PT100 resistance thermometer connection details
The Pt100 sensor is combined with the transmitter in one unit that's what the SEM206P is, and I have both 9208 and 9217 modules
Message 11 of 16
(3,695 Views)
Apologies but I am struggling to find an actual picture of the full unit, it is combined with a Pt100 sensor with the transmitter internally connected, so in effect all I have to connect up are the positive and negative terminals to somewhere??
Message 12 of 16
(3,693 Views)
Again apologies for my mistake, the SEM206P is not the total unit, I have a SEM206P which is connected to a Pt100 sensor in a combiened unit with the postive and negative terminals to connect.
Really should read what I am writing before I post.
Message 13 of 16
(3,692 Views)
Than you have 2 Options, both of them will work.
1) Using PT100 + Transmitter : Use NI 9208 : Connect (+) coming from the SEM206P to Vsup of NI9208 (19), connect (-) coming from the SEM206P to AI0 of of NI9208 (1) . Then use the sample program of NI 9208.
2) Using PT100 only : Use NI 9217 : Remove the transmitter connections of the PT100 sensor, then you will have 3 wires: Red, white and white. Connect Red to RTD0+  (1), connect white to RTD0- (2), connect second white to COM (3) . https://www.ni.com/docs/en-US/bundle/374187f/resource/374187f.pdf
Message 14 of 16
(3,691 Views)
All working fine now, just connected the Pt100 without the transmitter wired in.
Thanks again for your help tcanger, greatly appreciated.
Message 15 of 16
(3,679 Views)
not to mention, we usually struggle at the most simplest point, and people called experts are those who failed the most.
Message 16 of 16
(3,671 Views)
