SCXI 1303 generic voltage input

Hallo everybody,

 

I would like to use a SCXI 1303 module to acquire a signal different than the one from a thermocouple.

 

My signal is current 4-20 mA; I connected a resistor of 0.47 kohm to have a voltage signal as insput of my module.

I connected the signal to my module and I defined a channel in MAX (analog input 0-10 V). The problem is that the signal I read through the NI device is different from the real one (cross checked with a voltmeter). If for example the real signal is 9.5 V, the acquisition system read 8.1 V...

Any idea? Is it linked with any configuration of the device?

 

Thank you

0 Kudos
Message 1 of 3
(6,606 Views)

Hey pippo971,

 

were did you get the 8.1 V? In MAX or in LabVIEW?

 

You have a SCXI 1303 terminalblock, but on which SCXI-module do you put the terminalblock? Can you give us a overview of the measurement system?

 

Thanks, 

cheggers

Sascha
0 Kudos
Message 2 of 3
(6,584 Views)