02-25-2010 07:31 AM
I need to know what, or how to calculate, the accuracy of an SCC-RTD01 from the specifications and could use some assistance.
My total system will use a thin-film platinum RTD (100 Ω at 0°C, temp coefficient of 0.00385 Ω/Ω/°C), connected via 4-wire to the SCC-RTD01 installed in a SCC-68 I/O connector block and digitized by a PXI-6251.
NI's online accuracy calculator conveniently provides the calculated accuracy for the PXI-6251.
Any help is appreciated-
02-26-2010 02:10 AM - edited 02-26-2010 02:10 AM
The spec of the SCC-RTD01 tell me a 1.2% gain error 😮 as the biggest point. However with a RTD simulator this could be calibrated and compensated.
02-26-2010 07:41 AM
Thanks for the info on the RTD simulator. I was not aware of their existance - maybe our calibation guys have one...
Anyway, so I can estimate that the 1.2% gain error will be the majority of the error but I'd like to know (for my own informatoin) how I would include the +/- 250uV (RTI) for the offset error. The RTI part is confusing me.
Also, your RTD simulator leads me to a new question (I don't have the equiptment yet so I can't check myself). Can I store this calibration/compensation value provided by the RTD simulator somewhere in MAX or will I have to write code to do the compensation.
thanks-
02-26-2010 08:38 AM
I hope I am calculating something wrong but my estimation for the accuracy for the overall voltage measurement for the system is about +/- 2mV and a resistance accuracy of about +/- 2 ohm. This translates to an accuracy of only 5 deg. C. Can this be true?
02-26-2010 08:43 AM
If I remember right you can enter custom coefficients for the Callendar van Dusen equation. So it should be possible, however it will need some preprocessing to get these values.
02-26-2010 09:00 AM
03-01-2010 01:00 AM
Powerloos in the thermistor? Selfheating?
03-01-2010 07:29 AM
03-01-2010 08:19 AM
Even if you don't have a RTD simulator/calibrator , two 100R and a good voltage meter (4+ digit) can give you the same answers. Generous people also spend big Cs in parallel 😉
Connect both R in series to the current source and allow 20 min to settle. Measure alternativ with the SCC/DAQ and the DVM the 100mV and 200mV