I have an application using Hall effect current sensor that generates a ratiometric output voltage proportional to current.
The output of the sensor is input to a NI 9205 in a cRIO. Is it possible for the sensors supply voltage to be derived from the same voltage source as the NI 9205 A-to-D converters reference voltage to eliminate errors due to power supply fluctuations.
Thanks
07-12-2010 11:40 AM
Hi blind1-
What sensor are you using? What exactly is the concern? If you are worried about using the same ground reference, you can certainly ground your sensor using a ground terminal on the 9205. If you are using a bridge-based sensor, you can use a second analog input channel to detect the voltage at the bridge and account for that in your ratiometric output by dividing by the 'actual' voltage.
I hope this helps. Best of luck with your application!
07-12-2010 12:19 PM
I am using Allegro ACS712. My concern is output error . Trying to measure current within 0.5% accuracy.
That looks like one option to use a second analog input to measure Vref at the sensor.
The other option is to Calibrate my system using the scaling factors in software and HOPE Vref doesn't drift.
Thanks