How To Calculate RMS Voltage in VeriStand
I am looking to calculate RMS voltage of a scaled AC 60 Hz waveform in VeriStand. We have 120 VAC outputs connected to a load resistor and are using a current transducer to output a scaled analog voltage into a NI-9205 module. In VeriStand I am getting instantaneous values but would like to calculate RMS voltage and then threshold it to detect binary on/off of these outputs. In the calculated channels I see an option to do an average with n samples, but this is not helpful for a sinusoidal waveform.
Chase Fearing
Test Engineer, Certified LabVIEW Architect
(830 Views)
The easiest way would be to just buy and RMS transducer.
https://www.crmagnetics.com/ac-voltage-transducers/true-rms/single-phase/cr4511
for example.
Otherwise you are going to have to develop a model to find peaks and take the sqrt of 2.
(824 Views)
The better is to compute the RMS in the CRIO FPGA. If you need high precision the better is to use a sine interpolation computation. If you can't, you have to do the same in a VS model.
HAGD
(788 Views)