10-07-2020
11:28 AM
- last edited on
11-03-2025
03:24 PM
by
Content Cleaner
On bellow page there is a table with Default Counter/Timer Terminals of the PXIe-6341
https://www.ni.com/documentation/en/pxi-multifunction-io-module/latest/pxie-6341/pinout/
Most of the Terminals are assigned TWICE to a Counter I/O... what does that mean?
Solved! Go to Solution.
10-07-2020 01:18 PM
It's just additional labeling to help people make correct encoder connections. The SRC, GATE, AUX, and OUT pin designations tell you about the connection on the counter itself. The A, B, Z pin designations tell you about the connection on the encoder side.
Encoder ch A should be connected to a counter's SRC pin, ch B to AUX, and ch Z to GATE. And that's what the redundant pin labels are trying to make clear.
-Kevin P
10-08-2020 02:14 AM
Thanks a lot for that perfect explanation! 😃
10-09-2020 06:44 AM
Using your Explanation I made a spreadsheet with the pinout of PXI-6341 with TB-2706:
https://forums.ni.com/t5/PXI/NI-PXI-6341-16-AI-2-AO-24-DIO-with-TB-2706-Terminal-Block-Pinout/