1. Yes you can reset all the encoders' counters to zero at the same time, but it'll involve lots of wire.
2. It sounds as though the only time you care about the value in the 6 test encoder counters is when the master encoder reaches a specified value. Then immediately after capturing the six test encoder values, you'd like to reset them to zero. Is this correct? I'm further supposing that you aren't needing to buffer the master encoder position -- you just need to trigger the capture & reset when it hits a target, right?
Here goes then:
3. Setup 3 buffered position acquisitions on each of your 6602's, and wire the A & B channels of your 6 test encoders to their corresponding Source and Aux/UpDn pins. Each of the counters' default gate pins needs to be physically wired to the output of a counter whose function is explained below. Setup the counters to enable Z-channel indexing with a reload value of zero. Setup gating to use RTSI, say RTSI 6 with 'Counter Gate (NI-TIO).vi' More on this below also.
4. A counter needs to be setup that will fire a trigger-like signal when the master encoder reaches a specific value. Wire the master encoder to a counter and configure for (non-buffered) position measurement. Bring its Z-channel into the gate pin and enable Z-channel indexing, but don't use zero for a reload value. The correct value will depend on whether the master typically counts up or down.
Supposing you want to "fire" when the position is 1000 counts beyond the Z-index position, then you would set the reload value to 1000 if counting down or to (2^32 - 1000) if counting up. That way, 1000 counts after the Z-channel index, the counter value will be zero.
5. On this same counter, setup the output to *pulse* upon reaching terminal count, and route the output onto RTSI 6, as presented earlier. Here it will act as a gating signal to latch the test encoders' positions at the instant that the master reaches the desired value.
6. Setup another counter for retriggered pulse generation. Use the prior counter's output as the gate signal. Might as well config for RTSI 6 since it's already there anyway and doesn't require a screwdriver. Setup a minimal delay time and a reasonable pulse time. Physically wire the output of this counter to all the default gate pins of the 6 test encoders. While it's high, all the test encoder counters will get reset to zero.
7. Summing up steps 3-6. When the master reaches a precise specified position relative to its Z-index position, a counter will generate a pulse that is used to buffer the positions of the 6 test encoders. The same pulse will trigger a single pulse from another counter, which is wired as the Z-channel index of the 6 test encoders, resetting their values to zero. The wiring and config involved guarantees that the position values are latched before being reset to zero.