HI,
I have NIcDAQ chasis along with NI 9401 AI(0-10V). I want to scale these voltage signals to Pressure Signals(bar).
At 2 Volts the Pressure is zero bar and at 10Volts the pressure is 100 bar. After reading the signals I am scaling the signals in labview(calculating). Doing so I get a lot of spikes. Please help me in this.
I have attached a vi showing what I am doing. I am be wrong as I am new to labview. I tried DAQmx custom scaling but couldn't work it out.
Thanks in Advance.
04-05-2019
02:46 AM
- last edited on
01-11-2024
02:39 PM
by
migration-bot
Hey himanshu,
The NI 9401 is a digital input module incapable of collecting analog data. You shall use one of the voltage input modules for this application: https://www.ni.com/en-us/shop/category/voltage.html
In case you are using a proper card I would recommend opening up an example VI from Help -> Example finder, I particularly recommend the "Voltage - Continous Input.vi" from the DAQmx library.
Once you can collect the data itself, and the example VI will do most of the job, you can create a scaling using the following equation:
return (x - in_min) * (out_max - out_min) / (in_max - in_min) + out_min;
Of course you should implement it using some simple VIs and it is elegant to put this step into a subVI.
And thats it, done!
04-05-2019 02:54 AM
Hey again,
I could not resist and made the scaling subVI, find the image attached:
Cheers!
04-05-2019 06:21 AM
I have one more query.
I am write the voltage Signals and the pressure Signals to a measurement file. And I want absoulte time and relative time in the same file. Please help
04-10-2019 04:50 AM
If I were you I would use the TDMS file format to store the data. The collectd waveforms do have the starting time and the delta T embedded, thus the absolute time value can be calculated from there. Also you can make a simple channel for the relative time witch is basically a number starting from 0 and incrementing in every iteration with the periodic time.