OPC with datasocket/itools

Hi, I have a problem with Datasocket and Dasylab 8.0 when using OPC to talk to Eurotherm PID controllers using the Eurotherm OPC server.  Dasylab sends out a 0 when the worksheet is first run and then the correct variable value. This causes problems when you have a full scale overtemperature alarm set up on the controller.  The alarm setpoint is momentarily set at 0, which causes the alarm to trip.

Does anybody have any ideas on how to stop Dasylab/Datasocket from doing this...

regards....

Philpo