01-29-2013 04:26 PM
Our team is attempting to flash a new firmware on the 8-Slot cRio with the windriver setting. When flashing the cRio imager software hangs at the reboot of the cRio. When it hangs, the status light blinks twice every two seconds. When power cycled the cRio continues this two blinking pattern. Any suggestions?
01-30-2013 08:48 AM
The reboot of the cRIO occurs when the IP gets changed.
Often a directly connected laptop will lose connection with the cRIO during the IP change, because it can't handle the IP quick change.
The common solution is to interpose a router or switch that will maintain the connection for you during the change. Those devices are better suited to changing IP addresses.
The two yellow blinks means there is no image/OS on the cRIO, and that's because the image gets downloaded after the IP change. Since your laptop lost connection during the IP change, it never got an opportunity to download the cRIO image.
01-30-2013 10:25 AM
When our cRio hung during reboot, we flipped the safe mode DIP switch on the front of the cRIO and rebooted and it worked fine.
01-30-2013 01:14 PM
Switching to a router or switch as Mark suggested is a great first step. You can also try putting the cRIO into Safe Mode as noted by albfrc.
If you still have an issue, you might want to try checking your network settings (IP address, subnet mask) to make sure they are properly configured. The Driver Station software will automatically set your IP address if you enter your team number. But you can also manually set your computer's IP address if needed. This is described in the FRC Getting Started Guide, page 16.
Also, make sure you do not have a Gateway or DNS Server defined on the cRIO or host PC (these should be blank or 0.0.0.0).
01-30-2013 09:46 PM
Though I will next try tomorrow, I can try to give additional information. I think it may be the fact that my computer uses predefined DNS servers. I will attept to turn these off on my next attempt.
In addition, I will go into more detail on how the imaging software behaved:
I can find the cRIO, and can successfully connect to it.(I opened up ftp with cmd and successfully connected to the IP address.)
When attempting to reformat the cRIO with the supplied .zip file, the software successfully reads the DIP switches, then appears to successfully transfer the OS file to the cRIO. The program then hangs when trying to reboot the cRIO over the network. During this time the cRIO flashes 2x. I had once tried to do a manual power cycle. This action did nothing.
The cRIO is connected over the supplied Ethernet brige. My windows 7 laptop is connected to the brige with a standard Ethernet cable.
My laptop is using the correct IP address when updating the OS of the cRIO.
I will attempt to remove my DNS servers, but I have a feeling this will not do anything consitering the fact that it is a direct IP connection, thus the DNS servers should not be contacted at all.
EDIT: Should I try manually sending the .zip over FTP?
01-31-2013 11:53 AM
You can also try manually putting the cRIO into safe mode before reimaging. With a cRIO-FRC I (8 slot), you can turn on the Safe Mode dip switch and restart the controller. For the cRIO-FRC II (4 slot), you can do this by holding the reset button for 5 seconds. The Status light should blink 3 times to indicate safe mode.
It's also a good idea to check your Windows Firewall and antivirus settings to make sure they aren't causing communication issues.
01-31-2013 05:03 PM
Thank you for all of the suggestions, but I have not been able to continue. The program still hangs when trying to reboot.To reiterate I have:
I have also tried reading the built in serial console, but the usb converter status lights tell me nothing is being transmitted.
I'm really stumped on this one. Any help at this point would be very very greatly appriciated.
01-31-2013 05:23 PM
To enable the Serial output, you need to turn on the Console Out dip switch and restart the controller. This is the cRIO-FRC I with dip switches, correct? (See the procedure for 4 slot cRIOs below.)
To clarify, do you have anything but 0.0.0.0 defined as your computer's gateway? For direct connection and switch this should be the case.
Have you tried finding the cRIO in Measurement & Automation Explorer (MAX)? This might help us troubleshoot the connections issue. For more help with this, you can call NI FRC support at 866-511-6285 between 1-7 PM Central M-F.
(On a four-slot, Safe Mode can be reached by holding down the Reset button for 5 seconds, releasing it, and holding the button down for 5 more seconds. This process puts the cRIO-FRC II into Safe Mode with an IP Reset and Console Out turned on.)
01-31-2013 05:48 PM
This is the first edition cRIO. I had turned on the console out dip and power cycled the controller. The computers gateway shows no numbers.
I successfully connected over MAX. Here are some important system parameters:
System Settings:
IP Address: 169.254.62.215
System State: Inconsistent IP Settings
Network Settings:
Configure IPv4 Address: Static
IPv4 Address: 10.37.77.2
Subnet Mask: 255.255.255.0
Gateway: 0.0.0.0
DNS Server: 0.0.0.0
Throught MAX I have been able to connect, and set parameters like IP addresses. Terrific progress! Any details on Inconsitent IP Settings?
01-31-2013 06:33 PM
It sounds like the network settings are not saving properly. This happens when the host PC is statically set and the cRIO is using a link-local address (169.254.x.x).
Try changing your computer's IP address to match the current cRIO subnet (something like 169.254.62.50) and then save the Network Settings. Once they apply correctly, you can move your host computer back to the correct IP address.