Mark,
The 9th channel is the CJC sensor channel and can be configured to provide the data in C, K or F. To change the range of the channel, right click on the FP-TC-120 and choose Edit This Device. Then click on Chanel Configuration. In the upper left corner, you will see a drop box with the text "Type 1: Analog Input", change the drop box to list "Type 2: Analog Input". You can now configure the range and attributes of the CJC channel.
From a LabVIEW perspective, there is no real difference in how the data is handled, just in how it is scaled. The FieldPoint VI's return data to a LabVIEW (or any other application) as scaled units. Thus if you have one FP-TC-120 (at 25 C) with the CJC set to K and a second FP-TC-120 with the CJC set to C, you will see a v
alue of 298 K from the first and 25 C from the second.
Note 1: "Type 1: Analog Input" corresponds to channels 0-7 of the FP-TC-120 and "Type 2: Analog Input" corresponds to channel 8 of the FP-TC-120. This can vary from module to module.
Note 2: The Thermocouple input channels (0-7), can be configured for C, F, K or V.
Regards,
Aaron
LabVIEW Champion, CLA, CPI