Hi Bobby-
It's pretty unlikely that you will be able to calibrate your FieldPoint modules with equipment you already have in your lab. FieldPoint calibration requires the FP-TB-CAL terminal block and Calibration Executive software. You may also need to acquire a different controller as the FP-1000 is required. Unless you already have a lot of this equipment on hand, your best option may be to send your modules to NI for calibration.
Hopefully this helps-