Hello,
There maybe a couple of reasons for this problem. First, make sure that you have configured the input channel correctly in MAX. Make sure that you have the channel check box selected, then change the Range to be 0-10V, then click Apply and then click Save. This will apply the new configuration to the FP module. Then, make sure that you have made your external connections correctly. For channel 0 connect the positive input to terminal 1 and the negative to terminal 18. More than likely, you did not have the correct 0-10V range set for the channel that you were measuring.
Regards,
Bill B
Applications Engineer
National Instruments