FP-AI-111 with 0-1mA inputs?

We need to connect several existing transmission line voltage meters with 0-1mA current loop outputs to our FP-AI-111, however, it is looking for 0-20mA, or 4-20mA.
Does NI have a module better suited for 0-1mA inputs?
0 Kudos
Message 1 of 6
(6,992 Views)
If you need more resolution, you may need to use a voltage input module and measure voltage across a shunt resistor placed in the current loop.  That is exactly what the current input module is doing.  Do you know the maximum loop resistance the existing transmission line voltage meters can drive?
0 Kudos
Message 2 of 6
(6,985 Views)
Hello,

All of our FP-AI modules have current inputs of 0-20mA, 4-20mA, and/or +/-20mA.  We do not have a module that is in the range of 0-1mA. 

Please let me know if there is anything else I can do for you.
Regards,
Ching P.
DAQ and Academic Hardware R&D
National Instruments
0 Kudos
Message 3 of 6
(6,983 Views)

Thank you. Max resistance the 0-1mA outputs can drive is 1K.

 Yes, resolution is our concern with connecting a max of 1 mA into the 0-20 input of the FP-AI-111. That's only 5% of the AI's range.

0 Kudos
Message 4 of 6
(6,975 Views)

With 1K precision series resistor you would generate 0-1V signal.  AI-112 just happens to have a 0-1V input range.  Smiley Happy

0 Kudos
Message 5 of 6
(6,972 Views)

Bingo!

Thank you very much, that sounds like the way to go.

0 Kudos
Message 6 of 6