FP-RTD-124

I have a new FP-RTD-124 module.
The measurement & automation explorer find the device.
I "run" the module in measurement & automation explorer, without PT100 4 wiring connected. I receive "Open wiring", this is normal. But one channel say sometimes "Out of range". What's the problem, nothing is connected to the module ?
0 Kudos
Message 1 of 4
(3,771 Views)
The [c]FP-RTD-122 and [c]FP-RTD-124 modules support two error codes; "Out of Range" and "Open RTD". Generally, if a channel is configured for temperature measurements and there is no wiring, you will see the "Open RTD" message. However, if the channel is configured for resistance, you will see the "Out of Range" message.

Regards,
Aaron
LabVIEW Champion, CLA, CPI
0 Kudos
Message 2 of 4
(3,771 Views)
All channel are configured for temperature measurements. All channel say "Open RTD", except one "Out of range" message.
0 Kudos
Message 3 of 4
(3,771 Views)
I plug in the FP-RTD-124 in an another terminal base and it's OK. It seem to be an problem with the terminal base. I send it to repair.
0 Kudos
Message 4 of 4