Hello TRCErin
We have a similar problem with cFP-AI-110 which freeze all channles, but after a longer, and not constant, time.
In MAX we read the same error, but it blinks from "unconfigured" to "successful" all the time, until a reboot of the unit.
That problem stays also after replacing all the hardware with a new one.
08-17-2005 06:19 AM
08-17-2005 03:00 PM
TRCE,
Fieldpoint modules are isolated from one another, so a spike on one will probably not affect the other. You, by chance, don't happen to have a themocouple extension wire connected to the bank that isn't connected on the other end with a probe? I have seen, especially around highly inductive loads (heaters coils), where an unterminated tc wire acts as an antennae and transmits noise to the Daq device. If this is the case, try removing these wires or terminating them with a tc probe.
Hope this helps,
Grub