I have a FP-1000 and FP-AO-200 connected together. MAX is able to find the FP-1000 and communicate with it. The FP-AO-200 POWER and READY lights are on.

MAX does not find the FP-AO-200 when I invoke "Find Devices". I can manually define it using "Create New Device". When I attempt to test a FP-AO-200 channel using the Write function in "Items Configuration" I get the following error message: "The module or item addressed does not exist".

I am also not able to write to any FP-AO-200 channels in LabVIEW 7.0.

Any ideas what is wrong?
0 Kudos
Message 1 of 3
(3,423 Views)
I would check the pins on the FP-1000, between the modules for bent or pushed in pins. Then, I would make sure the AO module is seated correctly in the Terminal Base.

If that's not it, try a different AO module and/or a different TB, to see which is the culprit. The AO module should show up when you do "Find Devices".
0 Kudos
Message 2 of 3
(3,423 Views)
Thank you Chad. It turned out both the TP And AO modules were bad. MAX was able to find both a TP and FP-AI-100 module that I plugged into the same terminal bases.

Dave Morris
0 Kudos
Message 3 of 3