Luis,
You can use the Optomux commands to reset the FP-1001 programmatically. The supported Optomux commands are described in the FP-1000/1001 Programmer Reference Manaul. There is a FieldPoint LabVIEW Optomux library, although it is only installed by default if you have LabVIEW RT installed. Otherwise, you will need to re-install NI FieldPoint and choose Custom installation. Select the LabVIEW FieldPoint Optomux support during the custom installation.
The correct command to reset the module is the !Z Reset.
Regards,
Aaron
LabVIEW Champion, CLA, CPI