FieldPoint Family
How to interface FP1000 with FP1001. I have a problem like, when i try to see the devices in Field point explorer i cannot see the device Fp1001 and modules connected to it . i can see only fp1000 and modules connected to it . what could be wrong
what are the possible problems faced while connecting FP1000 and FP1001.
I have connected FP1000 to the computer and FP1001 is connected to the FP1000 by RS485, I cannot detect FP1001 and the modules connected to it.
(3,372 Views)
Suresh,
There are several different reasons why you may be facing difficulties. First of all, the DIP switches on the FP-1000 and FP-1001 should be set so that the two modules have different addresses. As a side note, after changing the address/baud rate on FP-100X modules, you do need to power cycle the module to have the new settings take effect. A second reason that you may be having problems is that the RS-485 connection may be wired incorrectly. The Tx+ of the FP-1000, should be connected to Rx+ of the FP-1001, Tx- (FP-1000) to Rx- (FP-1001), Rx+ (FP-1000) to Tx+ (FP-1001), and Rx- (FP-1000) to Tx- (FP-1001). Additionally, depending upon cable length, you will probably need 120 Ohm terminating resistors wired (at both ends) between Rx+ and Rx- and a
second resistor between Tx+ and Tx-.
Aaron
LabVIEW Champion, CLA, CPI
(3,372 Views)