When a FP-TC-120 channel is configured for temperature measurement and a thermocouple type is specified, the module linearizes the measurement according to the NIST-175 standard for thermocouple characteristics which is based upon ITS-90.
Depending upon what communications methodology you are using from Visual Basic, you may or may not need additional scaling (presuming the channel is configured for temperature and not voltage measurements). If you are using OPC, then the data is already scaled and you do not need to do anything with it. If you are using the FieldPoint Optomux commands, you should scale the data as described in Appendix B of the FP-1000/1001 Programmers Reference Manual.
Regards,
Aaron
LabVIEW Champion, CLA, CPI