The FP-1600 module only transmits data when the data changes outside the configured deadband range for a channel. The default deadband of 0% means that if one reading is different by 1 bit from the previous reading it gets transmitted. However, if the previous reading was identical to the current reading, the data is not transmitted. What it sounds like is happening to you, is that the data on one channel is only slowly changing, and may not be changing enough for the configured deadband setting. A 1% deadband on the 0 - 10.4 Volt range, means that only changes greater than 0.104 Volts are transmitted. To view your deadband settings, open FieldPoint Explorer, right click on the FP-AI-110 in the left pane and choose Edit This Device, then click on the Channel
Configuration button.