Hi Jan. Welcome to the Fieldpoint world, congratulations on getting your other sensors working.
If the power supply you are using for the cFP controller is < 35 VDC, then you can use that power
supply for the LM35 as well. If it is not, you will need a power supply that is < 35 VDC for the LM35.
The LM35 data sheet lists 35 VDC as the maximum allowable voltage, while one of the diagrams
shows 4-20VDC; I don't know which is correct, I suspect the 35 VDC, but it has been a long time
since I used any of these devices. Whatever the maximum really is, as long as your cFP
controller supply voltage is lower, you can use it.
Connect the 'GND' terminal of your LM35 to the 'COM' terminal of one of your input channels.
Connect the 'Vout' terminal of your LM35 to the 'Vin' terminal of the input channel.
Connect the 'Vs' terminal of your LM35 to the 'Vsup' terminal of the input channel.
Connect the 'V' terminal of the connector block to the V1 (or V2, if that is where your power supply is
connected) of the cFP controller.
Connect the 'C' terminal of the connector block to the 'C' terminal on the cFP controller.
If your cFP controller power supply is > 35 VDC, you will need an external power supply that
is connected to the 'V' and 'C' terminals in the connector block, with no connection to the
controller terminals.
Configure the input channel for voltage, start with 0-15 V and work your way down.
This will allow you to measure positive temperatures up to the limit of the LM35.
cFP-AI-100 data sheet:
http://www.ni.com/pdf/manuals/370278a.pdfLM35 data sheet:
http://www.national.com/ds/LM/LM35.pdfHope this helps. Let us know how you make out.
Matt
edit: all the same applies to FP same as cFP.